Cannot match this UR5e acknowledgement to either plate-check attempt
EllaChen1164 · 2025年9月15日 14:09 UTC
20 条回复
Yes, startup line is present. Two runs, same local job label in each. I've marked the boundary.
19分Keep each run's event order intact. Don't let sorting timestamps erase that boundary.
8分Ask controls for the original capture fields, not only the exported acknowledgement column; a retained request counter may have been left out of the report.
12分Original capture requested. Current export has the job label and acknowledgement state, no request counter.
22分Also establish what the acknowledgement means in this interface, whether it confirms receipt or a completed inspection; the name alone leaves room for a second wrong assumption.
5分Who saw the physical plate after the timeout? The logs matter, but there might be an operator observation worth retaining without pretending it supplies an exact event time.
8分We had the same seductive arrows on another report; keep a copy of the original sources before anybody shifts timestamps to make the drawing behave.
2分Luis, operator remembers the plate still in the fixture but cannot say whether a check happened. Anika, original files are preserved. Jamie, acknowledgement means request accepted, with inspection result reported separately.
21分Then keep that result question separate. Accepted request isn't an accepted plate.
10分I have removed the report's link from acknowledgement to passed inspection. No result is matched to either attempt yet.
14分Did controls find an additional sequence field in the original capture, Ella? That could still help with attempt ownership even though it won't supply the missing inspection result.
22分There is a counter, but capture begins after the restart and nobody has its earlier value. Same job label still does not identify which request produced the retained acknowledgement.
20分Does the counter persist across that kind of restart? I would want controls to confirm that before interpreting the later value, even if the earlier one is unavailable.
9分And don't turn the operator's remembered plate position into a completion check; ours stayed in the fixture for both failed and successful attempts.
8分Understood, Anika. That observation stays as location only. Controls is confirming counter behaviour; I haven't used it to draw a new arrow.
21分Who owns the unresolved plate disposition while you investigate?
21分Quality owns it. They have left this plate unresolved, separate from work on future logging. Controls confirms the counter survives the application restart, but the missing earlier value still prevents the comparison we need.
11分For future attempts, agree an identity that both sides retain and include it in the saved result; preserve startup boundaries too, rather than relying on matching wall clocks later.
14分Those changes are being specified. Old acknowledgement remains unassigned. Thanks Daniel for starting with the restart boundary; it stopped the first report from looking much more certain than our evidence.