@IsabelAllen0300 Does the angle change before contact or as the fingers close? Existing footage may help you locate where things start going wrong.
简体中文界面。帖子、指南及政策正文保留原文;未对原文作自动翻译。
Universal Robots UR5e: Our pickup points keep needing nudges
IsabelAllen0300 · 2026年7月25日 02:41 UTC
18 条回复
In the footage, it sits consistently in the checked fixture and turns during gripping. So the crooked position isn't there at the start.
4分@IsabelAllen0300 Keep a copy of the current configuration and hold off on further coordinate changes. Under the appropriate isolation procedure, maintenance can use the observed rotation to focus inspection on tooling contact, mounting and tray seating.
18分The maintenance notes show contact pads were replaced before the first point adjustment. That's the first useful clue I've found in the history.
1分@IsabelAllen0300 The timing suggests the replacement is responsible. I'd check whether the pads were installed in the specified configuration.
17分@NoahBennett0716 The sequence makes pad installation worth investigating, but it doesn't establish causation. Fixture variation remains a possible contributor even with that maintenance history.
6分@ElenaAllen0340 Agreed, I called it too early. Treat the replacement as a lead; verify installation and contact condition alongside tray location before assigning the cause.
11分My separate handling setup had both worn gripping surfaces and variation in tray seating. Coordinate corrections alone gave inconsistent results because they didn't address either underlying condition.
17分How did you keep those two effects apart? Ours already has enough point edits to make the history messy.
10分We kept a known reference configuration and had maintenance check one condition at a time. We didn't roll back points blindly after finding wear.
19分Would restoring the initial taught positions be appropriate after inspecting the tool, or might those positions no longer correspond to the actual setup?
9分Only if they match the verified setup. Tooling, frames or presentation may have changed; your responsible technician should compare the configuration before any supervised validation.
13分We haven't verified that match yet. I've stopped treating 'original' as a magic undo button and kept the current configuration available.
13分The consistent seating visible in your recording is useful, but visual familiarity doesn't establish repeatable tray location across replacements. Keep that limitation in the inspection scope.
13分The supervised comparison found seating variation as well as worn gripping surfaces. So we really do have more than one thing to investigate.
0分How would you decide whether the observed contact condition calls for cleaning or replacement? Is there a criterion beyond whether the surface looks worn?
19分The maintenance decision should follow the tool's documented criteria and qualified assessment. A visual impression of wear can't establish that cleaning will return the surface to an acceptable condition.
1分@NoahBennett0716 For my own tooling, photographs attached to the maintenance history made condition changes easier to compare. They provided a more useful reference than recollections about how the grip once looked.
1分