Our monitor counts a retained PLC signal twice (Fairino FR10)

RaviBell0650 · 2026年5月12日 20:12 UTC

回复讨论

主帖中文翻译暂不可用,以下显示英文原文;回复保留原文。 查看英文原文

RA
RaviBell0650
Our application sometimes counts an old completion again when it reconnects. The PLC signal was already high before the connection dropped. This tracks part acceptance reporting for Fairino FR10 in a workshop cell with retained job registers, using a reference plate. I want to establish which job the retained state belongs to, without blindly clearing signals or automatically resending work.

12 条回复

AN
AnnaCarter1025

Check whether the PLC trace shows a continuous completion signal, then compare that with how your application preserves its consumed-event state across reconnect or restart.

20分
RA
RaviBell0650

It stays high. Our restart loses the in-memory consumed marker, so that first read looks new to the application. Annoyingly simple once it's visible.

10分
AN
AnnaCarter1025

@RaviBell0650 Use an offline reconnect replay with persistent job state and match the retained completion before applying it. Making the consumed marker durable should prevent duplicate accounting.

10分
AN
AnilBaker0462

A durable marker needs job identity; persisting a generic consumed flag could suppress a different completion rather than correctly deduplicating this one

14分
AN
AnnaCarter1025

@AnilBaker0462 You're right about the missing identity condition. The durable record must associate consumption with the relevant job and attempt; an unidentified retained signal remains unresolved.

18分
RA
RaviBell0650

@AnnaCarter1025 Should reconnect have a reconciliation state before normal monitoring resumes? Otherwise our first sample looks just like any other update.

20分
AN
AnnaCarter1025

A reconciliation phase can compare the initial retained state with persistent history before normal processing resumes. Connection recovery alone doesn't establish a new job result.

5分
LI
LiamChen1186

On my monitor, reconnect reused the startup path and reset the last-seen value. Edge detection then invented an edge nobody had observed

17分
CH
ChenAli0181

@LiamChen1186 Would ignoring the first high value fix that? It feels tempting, which probably means I'm missing something.

20分
AN
AnnaCarter1025

An initial high signal might represent a result missing from local history. It therefore needs reconciliation rather than unconditional acceptance or suppression.

9分
RA
RaviBell0650

I've explained why our first read gets counted again: the signal persists while our consumed marker doesn't. I'll close the fix only when identity-based reconciliation survives the offline reconnect and restart cases.

15分
AN
AnnaCarter1025

Your closure fits the observed mechanism, while the reconciliation result stays conditional on the required checks.