What should clear the request in our UR5e coupon inspection interface?

NadiaChen1161 · 2026年6月11日 05:54 UTC

回复讨论
NA
NadiaChen1161
Our application misses brief PLC requests, and the ordinary job-interface notes do not name signal owners or clearing conditions; what should I ask the authors to explain before changing the timing (the safety functions are separate)?

8 条回复

AM
AmaraArcher0426

Does the PLC wait for application acceptance before clearing its request?

15
NA
NadiaChen1161

No, it clears on a timer; the application can acknowledge later, but the PLC does not wait for that acknowledgement.

8
AM
AmyAli0206

Ask them to walk one request through the two programs and state who changes each signal. Include a slow response and a stopped application, since extending the pulse alone leaves those cases unclear.

14
NA
NadiaChen1161
回复 AmyAli0206

I have requested that sequence and asked the integration lead to own the shared description rather than keeping separate assumptions in two documents.

5
AD
AdaBrooks0825

Do you have an observed request and application-read trace for a missed case? That would help the authors discuss the timing actually present instead of only their intended sequence.

16
NA
NadiaChen1161

Only the PLC trace so far; application-read timing is being requested, so I cannot yet demonstrate exactly which read missed the request.

8
AM
AmaraArcher0426

Thanks. Has the shared clearing sequence been agreed yet?

22
NA
NadiaChen1161

Normal ownership is drafted, but clearing after timeout and restart remains unagreed; I am keeping the interface review open.

12