Our inspection request disappears before the application observes it

MayaBell0649 · 2026年8月17日 11:09 UTC

回复讨论
MA
MayaBell0649
The UR5e fixture-inspection application misses brief PLC requests. Who sets and clears each ordinary signal is undocumented. What should both authors agree before changing it? Independently engineered safety functions remain separate.

2 条回复

EM
EmmaBennett0724

Define one writer per signal, its event meaning and the observation permitting it to clear. Walk through delayed receipt, repeated requests and restart; simply making the pulse longer does not settle ownership.

16
MA
MayaBell0649

Both authors have a draft state table now. Receipt and completion are separate; clearing after restart is still disputed. No live interface change approved.

12