I cannot tell which FR10 revision these inspection screenshots belong to

LeahBaker0495 · 2026年8月16日 00:15 UTC

回复讨论
LE
LeahBaker0495
Our reference-plate inspection handover is mostly pendant pictures. No revision, called routines, fixture assumptions or expected ordinary PLC signals. What should I get from the integrator while they are still available?

1 条回复

LU
LuisAbbott0086

Start with the identified installed program set and a revision list, then walk one reference-plate cycle through its called routines and ordinary interface states. Keep the fixture drawing and inspection assumptions beside it. Screenshots can illustrate that walkthrough, but should not be the only place the next maintainer can discover what waits for what.