the screenshots end at a call i can't find

BenBench · 2025年6月16日 04:47 UTC

已关闭

主帖中文翻译暂不可用,以下显示英文原文;回复保留原文。 查看英文原文

BE
BenBench
I'm taking over the notes for our FR5 coupon inspection station. The screenshots show a call to a routine called CheckFixture, but I can't find that routine in the handover folder. The integrator is still around. I'd like to ask for the missing pieces without pretending I know which pieces there are.

18 条回复

VI
VictorAbbott0011
回复 BenBench

Have you got an actual program backup?

5分
BE
BenBench

There's a zip called handover. Mostly images and a PDF. I haven't found a program export inside it.

5分
VI
VictorAbbott0011
回复 BenBench

Then start by requesting that, matched to the installed version.

12分
LI
LiamBrooks0838
回复 BenBench

Ask the integrator to walk through the installed job with you and identify every external dependency. Include the ordinary PLC exchange and the fixture setup. A program export alone will not explain those.

7分
VI
VictorAbbott0011

No, but screenshots alone won't let him follow the missing routine either.

4分
BE
BenBench

I've asked for both. The integrator says CheckFixture is included in their working copy. They want to compare that copy with the station before sending it.

16分
VI
VictorAbbott0011
回复 BenBench

Sensible. Which copy produced your screenshots?

21分
EM
EmmaArcher0376
回复 BenBench

That comparison matters. I've been handed a perfectly readable folder from before a fixture change, then lost ages trying to understand why none of the sensor names matched. Nobody was hiding anything, they just exported the convenient copy.

5分
BE
BenBench

Victor, the screenshots came from an earlier trial. Integrator checked and said that directly. The station now uses a different fixture-check routine, so I was chasing an old name.

21分
NO
NoraAli0235
回复 BenBench

Are the old pictures being removed from the current handover?

8分
VI
VictorAbbott0011

Keep them archived, surely. Just don't present them as current.

19分
LI
LiamBrooks0838

An archive is useful if it is clearly separate. For the current handover, I would want the installed revision identified on the program export and on the explanatory notes.

4分
BE
BenBench

I've moved the trial material into a labelled old-trial folder. Current folder has the checked export, but the explanation of the PLC exchange is still missing.

7分
NO
NoraAli0235
回复 BenBench

Who is writing that missing explanation?

15分
VI
VictorAbbott0011

And can someone other than its author follow it?

22分
EM
EmmaArcher0376
回复 BenBench

Ben, don't be embarrassed to stop the walkthrough at the first unexplained signal. I nodded through one and then had to ask the same question by phone, with a queue of people waiting behind me. Not my proudest bit of preparation.

18分
BE
BenBench

Integrator is writing it, and maintenance will go through it with me. I already stopped at 'fixture valid'. It meant a stored setup check, not the live part-present signal I had assumed. Thanks, Emma. I needed that nudge.

18分
VI
VictorAbbott0011
回复 BenBench

That confusion belongs in the notes. You won't be its last customer.

12分

讨论已关闭

此讨论已连续六个月没有活动,现已关闭新回复。 最后活动: .