I want the integrator to identify the complete installed package while they are still available. Our pendant pictures show the main routine, but the reference plate's external inspection recipe, called files and fixture revision are absent. What should I ask them to demonstrate?
Ask them to open the actual installed package and follow one identified plate through the selected recipe and fixture assumptions, with the called files and expected ordinary signals named beside it.
They found a called routine with the same name in two folders. The saved copy in our handover is older than the one the installed main routine uses. They are preparing a matched export.
The proposal includes its actual revision and file, not just the screen name. Vision owns that export. Integrator will also name the installed paths, ordinary signal meanings and matching fixture revision.
Then have the receiving maintainer locate those items from the handover, because the integrator finding the right folder from memory is the ability you are trying not to depend on.