简体中文界面。帖子、指南及政策正文保留原文;未对原文作自动翻译。

FR5 inspection request disappears before our application reads it

AmaraAllen0339 · 2026年6月29日 08:31 UTC

回复讨论
AM
AmaraAllen0339
PLC sends a brief inspection request. Application sometimes misses it. Our ordinary job-interface notes do not assign signal ownership or clearing. Who should agree the retained exchange? Safety functions are separately engineered.

9 条回复

LI
LinBell0618

The PLC and application authors need one shared sequence. Define what request, receipt, completion and clearing mean, with the job identity carried through it. Making the pulse longer would not resolve the missing ownership.

18
AM
AmaraAllen0339

PLC author assumed the application clears the request. Application author assumed the PLC does after a timer. Neither description includes a receipt acknowledgement tied to the requested plate.

6
NA
NadiaChen1161

Can they walk one missed request through the recorded PLC change and application reads before redesigning it, so they agree which transition was actually missed?

16
LI
LinBell0618

Yes, Nadia. Preserve that trace as a failure example, then work through normal receipt and interrupted communication separately. A correct explanation of the old pulse does not itself define the replacement protocol.

4
AM
AmaraAllen0339

Trace shows the request high entirely between application reads. Integration lead now owns the shared sequence. PLC retains its identified request until matching receipt; application owns receipt. Completion remains a distinct result, not another name for receipt.

11
NA
NadiaChen1161

What happens when the application restarts after receipt but before saving the result, Amara?

4
LI
LinBell0618

That requires retained attempt state and a defined reconciliation path, including repeated request delivery. Otherwise the same identified request can start another inspection after the receiver forgets it already accepted the first one.

11
AM
AmaraAllen0339

Normal receipt ownership is agreed. Restart and interrupted completion remain open with both authors; the new description does not authorise automatic resubmission when the physical job state is uncertain.

21
LI
LinBell0618

Keep those open cases in the interface review and test plan. It is useful progress to settle normal ownership, but the replacement exchange is not ready merely because the pulse no longer disappears.