Should this retained UR5e completion add another housing?

BenBarnes0544 · 2025年10月8日 13:02 UTC

已关闭

主帖中文翻译暂不可用,以下显示英文原文;回复保留原文。 查看英文原文

BE
BenBarnes0544
Our report adds a housing after reconnect, although the completion was already high. How do I identify the result?

5 条回复

OM
OmarChen1187

Does the retained response include a job identifier, or have you only captured the completion bit? A high bit alone will not identify the housing inspection.

17分
BE
BenBarnes0544

Only the bit in our monitor log. The PLC has more registers. Thank you.

21分
OM
OmarChen1187

Ask the controls maintainer which registers describe the completed job, including whether they remain valid together across reconnect. Don't assume the current job register necessarily describes the old completion.

23分
BE
BenBarnes0544

Asked for that mapping. Counting is paused while we identify the retained result.

14分
OM
OmarChen1187

Keep the earlier saved result available for comparison too. Once you identify it, the reporting side must recognise a repeated delivery rather than add another accepted housing.

15分