Duplicate inspection count after reconnect

LeoBrooks0797 · 2025年9月22日 18:50 UTC

已关闭
LE
LeoBrooks0797
We get an extra accepted housing on the UR5e inspection display when the application reconnects. Same retained job number, completion already high. The database still has one result, so I think the screen is adding the reconnect message as another part. Where would you put the check?

6 条回复

LE
LeoChen1145

At the result entry as well as the screen. Have you actually checked the stored result rows, or just the total shown in another window?

9
LE
LeoBrooks0797

Actual rows. One accepted result for that job. Two entries in the display's little event list, one from each connection. The counter is the length of that list

21
LU
LucyBrown0915

Then stop treating that list as production quantity. It includes connection events dressed up as results. You can show a previously completed job after reconnect without counting another housing.

15
LE
LeoChen1145

Lucy, would you hide the repeat in the event list? I'd leave it visible but say it was loaded again. Handy when somebody says the display jumped.

7
LU
LucyBrown0915

Leave the history visible. Give the reconnect entry different wording and build the quantity from accepted result records. And check whether job numbers can repeat after a restart before using the number alone as the key.

17
LE
LeoBrooks0797

Counter now comes from the saved results in our replay test. The repeat entry says restored result. No extra housing counted there. Restart identity still needs answering before we call it fixed.

22