简体中文界面。帖子、指南及政策正文保留原文;未对原文作自动翻译。

Connector unloading stop with no readable FR5 message

AlexBaker0472 · 2025年9月10日 15:27 UTC

已关闭
AL
AlexBaker0472
Separate from my sleeve-loading ticket: our FR5 connector-unloading job also pauses, and its clip misses the message. Seller on Alibaba asks for more information. I want this report kept apart from the sleeve fixture, not diagnosed from its unfinished evidence.

5 条回复

FI
FionaAllen0325

Put connector unloading and the fixture identifier at the top. Then send one dated occurrence with the readable message, active step and matching logs. Make clear that the sleeve report is a different job, not a previous diagnosis of this one.

15
AL
AlexBaker0472

Fixture C6. New capture says waiting for outgoing clearance, step 18. Matching records sent under the connector ticket. Still don't know which device supplies that clearance.

2
FI
FionaAllen0325

Ask the controls contact to identify the expected condition and source for step 18 on that program revision. No point inspecting the sleeve fixture's detector just because someone already has its drawing open.

7
AL
AlexBaker0472

Controls identified the receiving pocket's clear confirmation. Maintenance is arranging a capture of that state at the next occurrence. No cause established yet, but the two tickets now have their own attachments.

11
FI
FionaAllen0325

Has the next shift got the receiving-pocket name and capture request too? The technical answer won't help much if the next clip is another close-up of the arm.

7

讨论已关闭

此讨论已连续六个月没有活动,现已关闭新回复。 最后活动: .