When should our FR10 inspection request be cleared?

JasperBrown0899 · 2026年6月9日 08:59 UTC

回复讨论

主帖中文翻译暂不可用,以下显示英文原文;回复保留原文。 查看英文原文

JA
JasperBrown0899
I need signal owners for our training cell. The application misses the PLC request pulse. Who should clear it after acceptance? This is the job interface, separate from safety.

8 条回复

TO
TobyAllen0318

Does the application send any acknowledgement that the PLC actually waits for?

17分
JA
JasperBrown0899

It sends one. The PLC clears request on a timer without waiting for it.

4分
TO
TobyAllen0318

Then ask the authors to draw what acceptance should do before choosing a longer timer; it needs to work when the application is slower than expected too.

21分
AL
AlexBell0646

Who wrote the current interface? They should help explain the timer.

19分
JA
JasperBrown0899

Two contractors. Each thought the other had written the sequence description.

20分
PR
PriyaAdams0133

I'd sit both down with one missed request. I don't know their intended protocol, but the empty space between their documents is now your support workload. It needs an owner beyond commissioning

13分
TO
TobyAllen0318

Have either of them supplied the acceptance and clearing sequence since you asked?

10分
JA
JasperBrown0899

Only a list of signal names so far. Still asking for the sequence.

23分