简体中文界面。帖子、指南及政策正文保留原文;未对原文作自动翻译。

When should our FR10 inspection request be cleared?

JasperBrown0899 · 2026年6月9日 08:59 UTC

回复讨论
JA
JasperBrown0899
I need signal owners for our training cell. The application misses the PLC request pulse. Who should clear it after acceptance? This is the job interface, separate from safety.

8 条回复

TO
TobyAllen0318

Does the application send any acknowledgement that the PLC actually waits for?

17
JA
JasperBrown0899

It sends one. The PLC clears request on a timer without waiting for it.

4
TO
TobyAllen0318

Then ask the authors to draw what acceptance should do before choosing a longer timer; it needs to work when the application is slower than expected too.

21
AL
AlexBell0646

Who wrote the current interface? They should help explain the timer.

19
JA
JasperBrown0899

Two contractors. Each thought the other had written the sequence description.

20
PR
PriyaAdams0133

I'd sit both down with one missed request. I don't know their intended protocol, but the empty space between their documents is now your support workload. It needs an owner beyond commissioning

13
TO
TobyAllen0318

Have either of them supplied the acceptance and clearing sequence since you asked?

10
JA
JasperBrown0899

Only a list of signal names so far. Still asking for the sequence.

23

参与讨论

欢迎来到 Application Robot

所有人都可以阅读论坛。登录或注册后即可发起讨论、回复或上传照片。

忘记密码?

注册账号即表示你同意我们的 使用条款 社区准则。请阅读我们的 隐私政策 ,了解我们如何处理你的信息。