When should our FR10 inspection request be cleared?

JasperBrown0899 · 9 Jun 2026, 08:59 UTC

Reply to discussion
JA
JasperBrown0899
I need signal owners for our training cell. The application misses the PLC request pulse. Who should clear it after acceptance? This is the job interface, separate from safety.

8 replies

TO
TobyAllen0318
Replying to JasperBrown0899

Does the application send any acknowledgement that the PLC actually waits for?

17 points
JA
JasperBrown0899
Replying to TobyAllen0318

It sends one. The PLC clears request on a timer without waiting for it.

4 points
TO
TobyAllen0318
Replying to JasperBrown0899

Then ask the authors to draw what acceptance should do before choosing a longer timer; it needs to work when the application is slower than expected too.

21 points
AL
AlexBell0646
Replying to JasperBrown0899

Who wrote the current interface? They should help explain the timer.

19 points
JA
JasperBrown0899
Replying to AlexBell0646

Two contractors. Each thought the other had written the sequence description.

20 points
PR
PriyaAdams0133
Replying to JasperBrown0899

I'd sit both down with one missed request. I don't know their intended protocol, but the empty space between their documents is now your support workload. It needs an owner beyond commissioning

13 points
TO
TobyAllen0318
Replying to JasperBrown0899

Have either of them supplied the acceptance and clearing sequence since you asked?

10 points
JA
JasperBrown0899
Replying to TobyAllen0318

Only a list of signal names so far. Still asking for the sequence.

23 points