Sleeve tilts despite the tray being located

LucyAbbott0045 · 2026年3月18日 18:00 UTC

已关闭

主帖中文翻译暂不可用,以下显示英文原文;回复保留原文。 查看英文原文

LU
LucyAbbott0045
Our FR5 sleeve tilts during grip closure. The tray location checks correctly; another pickup edit is being suggested.

6 条回复

SA
SamBell0681

Check how identified sleeves sit before closure and compare the actual finger contacts with the intended assembly. Have those contacts been changed recently, or is the tilt new with the current sleeve stock?

22分
LU
LucyAbbott0045

One finger contact was replaced. Earlier sleeves tilt too. Maintenance is checking the fitted contact.

8分
SA
SamBell0681

Give maintenance the replacement identity and the saved point changes together. A replacement history can narrow the search, but the actual fitted geometry still needs comparing before choosing which settings belong with it.

23分
LU
LucyAbbott0045

The replacement contact is correct but wasn't fully seated on its mounting. Maintenance has corrected that.

15分
LU
LucyAbbott0045

Programmer is reviewing the accumulated edits. Full transfer checks have not happened yet.

20分
SA
SamBell0681

What prevented it seating, Lucy? The handover should explain that finding so the next replacement does not start the same series of pickup corrections.

23分