I'm reviewing our non-safety job handshake for part inspection with Universal Robots UR5e in a PLC-coordinated fixture inspection cell, using a reference plate. The PLC sends a brief request, and our application sometimes misses it. I can't find anything clear about who owns each signal or when it gets cleared. Safety functions are independently engineered; this is the ordinary job interface.

7 条回复

NO
NoraAllen0322

Does your trace show when the PLC request is raised and cleared relative to application polls, including which side performs the clearing?

0
AM
AmaraChan1122

Our trace shows it rising and falling between two polls. The PLC clears it without an observed acknowledgement. No wonder the application misses it.

7
NO
NoraAllen0322

Take an ownership table and a retained-request proposal to the interface owner. A request held until matching acknowledgement should settle the handshake in an offline review.

15
NO
NoahArcher0368

@NoraAllen0322 Holding the request addresses the missed pulse, but it doesn't settle the interface. A retained request needs identity and restart rules to avoid being mistaken for new work.

5
NO
NoraAllen0322

@NoahArcher0368 Yes, I overstated that. Retention addresses the missed pulse. The offline review also needs matching identity, reset ownership and restart cases before the design is complete.

17
AM
AmaraChan1122

@NoraAllen0322 The missed-request diagnosis is settled for this trace. Completing the handshake fix still depends on the interface owner's assessment of signal ownership and the offline transition cases.

6
NO
NoraAllen0322

That diagnosis fits the trace, and you've kept the implementation claim dependent on the interface review.

17