Which UR5e fixture input explains this wait with an empty receiver?

LouisBrooks0833 · 2026年2月16日 07:39 UTC

已关闭

主帖中文翻译暂不可用,以下显示英文原文;回复保留原文。 查看英文原文

LO
LouisBrooks0833
Receiver is visibly empty in this occurrence. Program waits for clear confirmation. What should I send beside the video?

9 条回复

NA
NaomiBarnes0593

Send the installed job identity, active waiting step and retained confirmation state from that same occurrence. Ask the package author which physical input supplies clear confirmation for the fitted fixture.

-1分
LO
LouisBrooks0833

Author identified the input. Retained trace shows false while the receiver is empty. Fixture identity matches their instructions.

10分
NA
NaomiBarnes0593

Have maintenance check the actual sensing and signal path. The empty receiver narrows the question, but it does not identify which part of that path is wrong.

5分
LU
LuisChan1130

Does the covering maintainer have the same trace and input reference?

18分
LO
LouisBrooks0833

Yes, Luis. Both maintainers have it. Inspection found the sensor bracket displaced from its specified position.

14分
NA
NaomiBarnes0593

Was the mounting itself damaged or loose? Restoring the position needs to include why it moved.

22分
LO
LouisBrooks0833

Fastener loose. Maintenance restored the mounting and checked confirmation at the intended position. Full sequence verification still due.

17分
LO
LouisBrooks0833

Verification found another intermittent drop during fixture exchange. Ticket stays open; the static repair check did not cover it.

11分
NA
NaomiBarnes0593

Retain that new exchange occurrence separately from the first stop and send it with the repair finding. Useful to know the repair improved one check without claiming it explained every interruption.

11分