Our FR10 handover shows a call to a routine nobody included

AnikaAdams0160 · 2025年10月2日 03:55 UTC

已关闭
AN
AnikaAdams0160
The inspection handover has pendant screenshots showing a call to a fixture-check routine, but not that routine or its revision. I'm trying to get the missing dependencies while the integrator still remembers our housing station.

9 条回复

HA
HassanBrown0878

Is there a full program export, or only pictures?

12
AN
AnikaAdams0160

Only pictures in the handover folder. Controls says an export exists elsewhere, but nobody has matched it to the commissioned version yet.

14
LE
LeahBennett0756

Ask the integrator to reconcile the export with the commissioned programs, including called routines, configuration, fixture assumptions and expected ordinary PLC signals. More screenshots will not make that package reproducible.

15
HA
HassanBrown0878

Leah, should the spare fixture references be in that package too?

-3
LE
LeahBennett0756

Yes, where they are supported by the installed configuration, with any relevant revisions; a spare described only as housing nest may not carry the same assumptions as the fitted one

23
AN
AnikaAdams0160

Integrator matched the main program and supplied the called routines. One expects a different nest identifier from the stores sheet, so we're checking that before calling the handover complete.

8
HA
HassanBrown0878

That is exactly the sort of spare confusion I meant.

24
LE
LeahBennett0756

Anika, does the integrator's package also explain the ordinary wait conditions and where maintenance can see their sources? A complete file list alone will not help the person investigating a pause.

6
HA
HassanBrown0878

Did the nest identifier get resolved?

9