The FR10 sample request ends before the application reads it

PriyaAllen0307 · 2026年3月27日 00:31 UTC

已关闭

主帖中文翻译暂不可用,以下显示英文原文;回复保留原文。 查看英文原文

PR
PriyaAllen0307
Our PLC records a sample request pulse that the FR10 application never sees. Who should define its clearing condition?

10 条回复

JO
JonasArcher0372

Both interface authors. Ask each to write when request starts, what accepts it and what clears it. One shared sequence, with ownership named.

14分
PR
PriyaAllen0307

The PLC author says request is an announcement. The application author expects it to remain until accepted.

19分
AI
AishaBarnes0605

That disagreement is enough to explain why their expectations differ. Is acknowledge already defined, or is its meaning equally loose?

7分
JA
JasperChan1073

And what identifies the sample attempt? A fresh receipt of an old request must not look like another housing.

6分
JO
JonasArcher0372

Acknowledge needs its own clearing rule too. Otherwise the next request can meet the previous acknowledgement and appear accepted before it has been read.

8分
PR
PriyaAllen0307

Aisha, acknowledge means received in one note and completed in the other. Jasper, no attempt identity is documented.

11分
AI
AishaBarnes0605

Then they need to name acceptance and completion separately in the specification. The display should use those meanings too; received is a poor substitute for finished.

25分
JA
JasperChan1073

Thanks. Ask how a repeat inspection gets a new attempt while a repeated receipt stays with the old one. Both happen in real work.

23分
PR
PriyaAllen0307

I've returned those specific disagreements to both authors. The current ordinary interface is not agreed for commissioning.

4分
JO
JonasArcher0372

Include connection loss after acceptance in their review. That state needs an answer before anyone decides to clear or resend it.