Pickup edits after the finger pads were changed

AishaBell0692 · 2025年6月28日 08:06 UTC

已关闭
AI
AishaBell0692
I came onto nights to find two new pickup offsets in our FR5 housing-transfer job. The tray had not moved, but the finger pads had been replaced. One housing now sits slightly skewed in the grip. I have asked for a tooling check before another offset is added. What would you compare between the old and replacement pads? The old pair is still in the maintenance drawer.

3 条回复

DA
DavidAbbott0084

Compare how they sit on the fingers, not just the loose pad thickness. I inspected a tool where a replacement pad looked identical until its backing sat on a screw head. The grip was then beautifully repeatable in the wrong shape. Check the mounting faces and approved pad details with the tool isolated.

13
AI
AishaBell0692

We found one backing plate had not seated against the finger. Tooling corrected that and the integrator reviewed the added offsets before verification. The checked housing set now picks squarely. Thank you for pointing us toward the mounted pads rather than only measuring the loose ones.

13
DA
DavidAbbott0084

Was the backing plate wrong, or was something preventing it seating? Worth settling before the next pad change repeats the job.

18