One finger sits higher after our FR5 tooling service

GabrielArcher0366 · 2026年6月8日 14:04 UTC

回复讨论
GA
GabrielArcher0366
Our FR5 picks sleeves crooked since tooling service. Could the finger height explain the new point corrections?

4 条回复

BE
BethAbbott0063

It could, but don't diagnose from appearance. Can I ask whether maintenance compared the fitted fingers and mounting faces with the approved tooling drawing under the normal isolation procedure?

7
GA
GabrielArcher0366

They found different finger revisions fitted together. The older one has a different locating shoulder.

10
BE
BethAbbott0063

Mixed tooling is a concrete finding. Have the correct set fitted and the setup verified before deciding which point edits belong. Don't blindly keep compensation for the wrong fingers.

10
GA
GabrielArcher0366

Matched set fitted. Integrator is checking the accumulated edits before returning it to production.

22