FR5 housing stop hidden behind the summary screen

MayaChen1171 · 2026年4月20日 12:59 UTC

已关闭

主帖中文翻译暂不可用,以下显示英文原文;回复保留原文。 查看英文原文

MA
MayaChen1171
Our imported FR5 package pauses during housing loading. Forty-one days on the seller's support ticket and my video mostly shows the operator reading the summary screen. I have the job version and the housing fixture identity. Which observation would actually show what the application is waiting for?

20 条回复

AA
AaronBaker0436

Can the application maintainer show you the active step and its expected confirmation? That would give your next report a target instead of another view of the stopped arm.

7分
MA
MayaChen1171

Maintainer says the step is waiting for fixture seated. The housing looks down in the nest in my recording. I don't have the underlying indication in shot.

18分
WI
WillCarter1009

Ask what detects seated on that fixture. It might not mean the whole housing is correctly down, even if the label suggests it.

10分
TH
ThomasBarnes0538

Will's question matters. A nicer video of the same summary won't recover an input nobody captured.

18分
MA
MayaChen1171

Maintenance identified the seating switch and the mapped indication for this fixture. They're comparing a successful load and a stopped one with the application maintainer. No change to the wait.

23分
IS
IsaacBell0694

Are both examples using the same fixture insert? Your report needs that detail. Intermittent across two inserts can be a different problem from intermittent on one unchanged arrangement.

21分
MA
MayaChen1171

Same insert. We leave it fitted for this housing job.

23分
AA
AaronBaker0436

Good, that keeps the comparison manageable. Include how the housing sits at the switch end, not only its top face.

19分
MA
MayaChen1171

Comparison captured. Stopped housing is slightly high at the switch end. The other end looked seated, which is all my first video really showed.

3分
WI
WillCarter1009

That explains why I asked. Has tooling looked at what supports that end?

6分
MA
MayaChen1171

Tooling found a small packing strip left beneath the removable support after its last service. They're restoring the documented support arrangement and checking the affected housings.

20分
IS
IsaacBell0694

Was that service before the stops began?

8分
MA
MayaChen1171

Yes. Service entry precedes the first recorded stop. I can't date an earlier unreported pause.

11分
AA
AaronBaker0436

Send that entry with the comparison. It gives support something much more useful than 'sometimes stops'.

17分
TH
ThomasBarnes0538

And ask who checks the loaded sequence after tooling finishes.

8分
MA
MayaChen1171

Application maintainer and shift lead are doing that together. Tooling owns the support correction; I'm updating the report and the service handover.

6分
WI
WillCarter1009

A picture of the underside in that handover would help me. The strip was invisible in your original view, and another person could miss it during the next service.

17分
IS
IsaacBell0694

Will, a picture helps identify the arrangement. The service instruction also needs to say which supports belong there. Otherwise the photograph becomes another thing somebody interprets from memory.

8分
AA
AaronBaker0436

Maya, have the loading checks finished, or is the corrected fixture still waiting for that joint session?

24分
MA
MayaChen1171

Normal loading checks finished without the seating wait recurring. The joint session still has the interrupted-transfer recovery checks to complete. Support has the before-and-after comparison; I've added the support identities as well as the underside photo.

16分

讨论已关闭

此讨论已连续六个月没有活动,现已关闭新回复。 最后活动: .