Can the application maintainer show you the active step and its expected confirmation? That would give your next report a target instead of another view of the stopped arm.
简体中文界面。帖子、指南及政策正文保留原文;未对原文作自动翻译。
FR5 housing stop hidden behind the summary screen
MayaChen1171 · 2026年4月20日 12:59 UTC
20 条回复
Maintainer says the step is waiting for fixture seated. The housing looks down in the nest in my recording. I don't have the underlying indication in shot.
18分Ask what detects seated on that fixture. It might not mean the whole housing is correctly down, even if the label suggests it.
10分Will's question matters. A nicer video of the same summary won't recover an input nobody captured.
18分Maintenance identified the seating switch and the mapped indication for this fixture. They're comparing a successful load and a stopped one with the application maintainer. No change to the wait.
23分Are both examples using the same fixture insert? Your report needs that detail. Intermittent across two inserts can be a different problem from intermittent on one unchanged arrangement.
21分Same insert. We leave it fitted for this housing job.
23分Good, that keeps the comparison manageable. Include how the housing sits at the switch end, not only its top face.
19分Comparison captured. Stopped housing is slightly high at the switch end. The other end looked seated, which is all my first video really showed.
3分That explains why I asked. Has tooling looked at what supports that end?
6分Tooling found a small packing strip left beneath the removable support after its last service. They're restoring the documented support arrangement and checking the affected housings.
20分Was that service before the stops began?
8分Yes. Service entry precedes the first recorded stop. I can't date an earlier unreported pause.
11分Send that entry with the comparison. It gives support something much more useful than 'sometimes stops'.
17分And ask who checks the loaded sequence after tooling finishes.
8分Application maintainer and shift lead are doing that together. Tooling owns the support correction; I'm updating the report and the service handover.
6分A picture of the underside in that handover would help me. The strip was invisible in your original view, and another person could miss it during the next service.
17分Will, a picture helps identify the arrangement. The service instruction also needs to say which supports belong there. Otherwise the photograph becomes another thing somebody interprets from memory.
8分Maya, have the loading checks finished, or is the corrected fixture still waiting for that joint session?
24分Normal loading checks finished without the seating wait recurring. The joint session still has the interrupted-transfer recovery checks to complete. Support has the before-and-after comparison; I've added the support identities as well as the underside photo.