Get both programmers to write the intended state sequence together, including who sets and clears each signal. Making the pulse longer might hide the symptom while leaving the two sides with different ideas about what acknowledgement means.
our request disappears before the app sees it
RaviCarter0998 · 3 Mar 2025, 13:38 UTC
13 replies
PLC author means 'request offered'. App author means 'request accepted'. Same bit name, different contract.
8 pointsThere's a useful starting point. Define the meaning of each transition as well as its owner, including what remains asserted until the other side confirms it. Names alone won't resolve that disagreement.
10 pointsDoes the handover documentation include what should happen when the PC restarts halfway through, because we inherited a cell where both programs seemed reasonable individually and neither expected to meet the other's old signals on startup?
17 pointsInclude that in the contract. Normal completion, timeout, reconnect and restart need defined outcomes, not an instruction for the operator to keep clearing bits until the screen looks ready again.
18 pointsNo restart definition exists. We're reviewing the job state diagram before changing either program.
8 pointsUse the missed-request trace as one example for that review. It should explain the observed loss, and the revised design should specify how receipt is confirmed despite different polling schedules.
7 pointsOur training bench had two writers clearing one status bit. Could you check the actual writers against the proposed ownership table, not only the comments?
18 pointsFound an old cleanup routine clearing request too. Comments never mentioned it. Added to the review.
22 pointsThat sounds familiar; who will own the final interface document when both programmers leave, so maintenance has one place to look instead of choosing whichever comment seems newest?
23 pointsAssign a joint acceptance test too. Each side passing its own test isn't enough if the tests assume different clearing rules. Exercise the complete job interface, including interrupted exchanges, in a controlled environment before deployment.
1 pointsAnd make the operator recovery procedure match those tested states. Otherwise the software contract will be precise and the shift instructions will still say 'restart and try again', which reintroduces the uncertainty.
8 pointsControls lead owns the draft contract. Joint tests and recovery instructions pending; no live interface change yet.