Those two writers need sorting out first. Get both owners to draw who sets and clears each signal.
Our request is gone before the application notices
KaiBell0628 · 5 May 2025, 12:52 UTC
16 replies
Both owners say the other one clears it. Helpful.
5 pointsBring the code to the meeting.
10 pointsAnd take one captured missed request with you. It gives the discussion a real sequence to explain. Otherwise you can spend an afternoon agreeing how a handshake ought to work while leaving the existing one untouched.
23 pointsYes. Show them that occurrence.
10 pointsTrace found. PLC clears on its timer; app clears after acknowledgement. Two writers confirmed.
7 pointsNow agree one writer per field, plus the conditions for changing it. Put the agreement beside the signal list.
7 pointsDoes the application distinguish a newly issued job from a request still present after reconnect? Holding the request will help it see the value, but the job identity may still need attention.
3 pointsNo. It calls every first high reading a new job.
7 pointsThat needs a recovery rule too. The operator should not have to infer whether work was accepted before the connection went away. A retained job reference and a visible unresolved state are possibilities for the interface review.
20 pointsWe had a class exercise that looked perfect until we closed and reopened the monitor. It immediately submitted the same job twice. The students thought they had broken the robot. They had exposed a missing case in my example. Walk through a request missed entirely, a request accepted before disconnect and a result returned while the application is away. Ask what each side knows at every step. That is a useful lesson even before any code changes, and it gives whoever supports the cell a fighting chance of explaining a stuck screen.
5 pointsOuch. Yes, add those cases.
21 pointsAdded to the review. Nobody is changing the polling interval as the whole fix now.
17 pointsWho will own the remaining unresolved-job decision during a shift? The interface can display uncertainty correctly and still leave production waiting if no one is assigned to handle it.
18 pointsShift lead, with controls backup. Draft agreed; still needs the joint tests.
2 pointsPut those names on the handover. Otherwise it's back to calling whoever wrote the first version.