Can we stop nudging this pickup now?

AnikaBrown0943 · 26 Apr 2025, 21:12 UTC

Closed
AN
AnikaBrown0943
Our UR5e sleeve pickup is crooked again. Tray looks seated. Another point tweak proposed. I want the tool checked first

14 replies

AI
AishaBell0692
Replying to AnikaBrown0943

We found uneven finger wear after weeks of small teaching changes on a similar handling job. Ask maintenance to inspect the tool mounting, fingers and tray contacts under isolation, and save the current setup before anything changes.

5 points
AN
AnikaBrown0943
Replying to AishaBell0692

Saved it. Maintenance found wear on one finger, but the mounting checks were fine

21 points
AI
AishaBell0692
Replying to AnikaBrown0943

Compare the contact surfaces and part seating before deciding the wear explains the skew. Also note which sleeve and tray were involved, so the post-maintenance check can use an identified example.

14 points
AN
AnikaBrown0943
Replying to AishaBell0692

Same sleeve leans in one pocket but not the next. That complicates the finger theory

4 points
AI
AishaBell0692
Replying to AnikaBrown0943

It suggests the pocket deserves inspection too. The finger wear can be real without being the only contributor. Have maintenance compare the suspect pocket and the locating surfaces.

14 points
SA
SamBrooks0855
Replying to AnikaBrown0943

Can you compare that pocket with the same position on another identified tray? A static seating comparison should help before any further teaching changes.

-4 points
AI
AishaBell0692
Replying to SamBrooks0855

Yes, using the agreed inspection procedure. Record whether the sleeve leans before the fingers contact it; that separates part presentation from what happens during gripping.

8 points
CL
ClaraBaker0437
Replying to AnikaBrown0943

Was that lean visible before closing, or are we guessing from the finished grip?

15 points
AN
AnikaBrown0943
Replying to ClaraBaker0437

Before closing. Maintenance did the comparison with the tool clear. Pocket has a damaged insert

11 points
CL
ClaraBaker0437
Replying to AnikaBrown0943

Right, then you've got something better than 'robot seems off' to work with.

0 points
JU
JuliaAdams0152
Replying to AnikaBrown0943

Don't forget the worn finger while everyone celebrates the pocket. You found two things. Check both, then verify the setup as a whole. One satisfying explanation doesn't make the other observation disappear.

21 points
AI
AishaBell0692
Replying to JuliaAdams0152

Agreed. The repair plan should address both observations, with the responsible person reviewing any teaching changes that may have compensated for them.

6 points
AN
AnikaBrown0943
Replying to AishaBell0692

Both in the work order. Tray insert replaced; finger service and setup check still pending

11 points
AI
AishaBell0692
Replying to AnikaBrown0943

Leave the return-to-use decision with that final check. The next shift will need the approved tool and program combination, not only a list of parts that were replaced.

18 points