who clears this inspection request?

AnilBell0636 · 29 Oct 2025, 22:04 UTC

Closed
AN
AnilBell0636
I've got attempt identities covered on this UR5e inspection interface. The unresolved bit is earlier: the PLC clears its request on a timer, while the app thinks it clears after acceptance. No wonder the traces tell different stories. What's the cheapest way to put both owners in front of the same missing-request case? This is the job interface, separate from safety control.

5 replies

EL
ElenaBrown0949
Replying to AnilBell0636

Use a trace where the app polls either side of the request, and put the PLC timer transition on that same timeline. Actually, first ask both owners to label who writes each value. A shared diagram with two writers hidden in it is still sketchy.

8 points
AN
AnilBell0636
Replying to ElenaBrown0949

One writer each. PLC raises and clears request; app writes acceptance. The dispute is exactly when PLC may clear. I've drawn the app's delayed poll beside the current timer expiry.

10 points
EL
ElenaBrown0949
Replying to AnilBell0636

That should make the gap visible without buying faster hardware. Are they proposing to retain the request until a matching acceptance, and what do they expect to happen if the app never answers?

11 points
AN
AnilBell0636
Replying to ElenaBrown0949

Retained request is proposed. Unanswered request becomes a visible waiting fault needing the defined recovery, not permission to send another job. Restart handling still needs agreement; the timer argument is finally over.

25 points
EL
ElenaBrown0949
Replying to AnilBell0636

Post how the restart example goes. That is where a page can look empty while the PLC still has work pending, and somebody decides another click will help.

13 points