Can't sign off the insert selection yet

CallumCarter0969 · 10 Jan 2025, 02:48 UTC

Closed
CA
CallumCarter0969
I've got two nest inserts on my desk for an FR5 inspection station. Same outside shape, different relief underneath the sensor cover. Either insert will bolt down either way round. The screen asks the operator to select a part family. I can't sign that off as an insert check. Am I missing an obvious mechanical answer?

13 replies

RA
RachelArcher0435
Replying to CallumCarter0969

Make the wrong orientation physically difficult to install, if the tooling permits it. Selecting a family on a screen establishes what somebody intended, not what they fitted.

8 points
CA
CallumCarter0969
Replying to RachelArcher0435

Would one locating pin solve both? Or just the rotation?

14 points
RA
RachelArcher0435
Replying to CallumCarter0969

Only what its geometry distinguishes. If both inserts accept the same pin in the same orientation, you still haven't identified which insert is present.

4 points
CA
CallumCarter0969
Replying to RachelArcher0435

Toolmaker confirmed that. Offset locator for orientation is possible. Still looking at two interchangeable families.

2 points
RA
RachelArcher0435
Replying to CallumCarter0969

Then give identity its own check. The recipe should agree with the installed insert, and the response to an absent or unreadable identity needs defining too.

20 points
EL
ElliotChan1118
Replying to CallumCarter0969

Do your inserts stay with one part family? We had removable labels on teaching fixtures. Someone swapped a label to tidy the cupboard and the label check happily approved the wrong fixture.

6 points
RA
RachelArcher0435
Replying to ElliotChan1118

That's a good failure case for the design review. Reading a tag proves which tag was read. How it stays associated with the insert matters just as much as the reader.

12 points
IS
IsabelChen1170
Replying to RachelArcher0435

Plan how a replacement insert gets accepted as well. Our fleet tooling had a tidy normal workflow, then a spare arrived without its identity configured and nobody on shift knew who could authorise it. Downtime came from that missing handover.

2 points
RA
RachelArcher0435
Replying to IsabelChen1170

And don't let the replacement process become the everyday way to dismiss a mismatch. The normal screen should explain what's mismatched and keep the automatic job pending.

20 points
DA
DanLoop
Replying to RachelArcher0435

Your software also needs to reject an identity left over from the previous insert, unless removal and reinstallation reliably trigger a fresh check.

2 points
CA
CallumCarter0969
Replying to DanLoop

Good catch. Demo screen retains the last family after the fixture is removed. I've added removal and a swapped label to our test list. The inserts will each stay with one family.

9 points
DA
DanLoop
Replying to CallumCarter0969

Retaining the displayed family is not itself the defect; treating that retained value as current proof of the installed tool would be.

5 points
CA
CallumCarter0969
Replying to DanLoop

Yep, I described that badly. It still shows the old 'verified' state too. Toolmaker is revising the locator; software review is tomorrow. Thanks for giving me a specific failure to demonstrate.

8 points