the fr5 screenshots stop where the inspection recipe starts

OliverBrown0885 · 6 Feb 2026, 01:25 UTC

Closed
OL
OliverBrown0885
Our bracket-verification handover shows the main FR5 routine calling an inspection recipe. The recipe itself is not included. Neither are the fixture mapping or the program revisions. The integrator is still available. What should our maintainer ask for as one matching set, rather than another folder of pictures?

1 reply

HE
HenryAli0177
Replying to OliverBrown0885

Request the installed program package with called routines, external recipe files and their mappings, revisions, fixture assumptions and the ordinary PLC interface definitions. Include configuration needed to reproduce the installed software arrangement, not just source files. Then have the maintainer trace one identified bracket through recipe selection, request, receipt, result ownership and an interrupted case using that set. The integrator can answer omissions as they appear. Keep the independently engineered safety documentation identified separately; these job-interface notes must not be treated as its replacement.

15 points