detailed FR10 logs coincide with a telemetry screen that stops moving

QuinnChambers · 18 Aug 2026, 21:18 UTC

Reply to discussion
QU
QuinnChambers
Since I enabled detailed read-only logging, our FR10 telemetry display sometimes stalls while the log folder is busy; cell controls are separate, and although synchronous writes look suspicious I have not ruled out delayed acquisition, so what timing would separate them without adding more load to the same recorder?

4 replies

HE
HenryArcher0351
Replying to QuinnChambers

Measure acquisition, decoding, publication and file-write time separately with a monotonic clock. Keep that small timing record away from the suspect write path, and compare equivalent observations with detailed logging on and off. Also record the age of the displayed reading; a frozen screen doesn't establish an offline controller.

15 points
QU
QuinnChambers
Replying to HenryArcher0351

I'll separate those stages and use a bounded timing capture outside the detailed logger; no measurements back yet, and the existing screen does not make the age of its last reading obvious enough.

11 points
HE
HenryArcher0351
Replying to QuinnChambers

Fix that presentation expectation alongside the diagnosis. If you later move writes into a queue, decide its limit and failure reporting before calling it solved. A responsive screen with silently missing diagnostics would answer only half your original problem.

11 points
DI
DineshBell0647
Replying to QuinnChambers

Have the paired timings identified the long stage yet, or are you still working from the busy-folder observation?

-3 points

Add to the discussion