Fairino FR5: Who owns clearing the job handshake?

IsabelBaker0474 · 1 Jun 2026, 02:00 UTC

Reply to discussion
IS
IsabelBaker0474
Our application sometimes misses the PLC's brief request for fixture inspection. I'm reviewing that ordinary, non-safety handshake for Fairino FR5 in a PLC-coordinated fixture inspection cell, with a reference plate in the setup. Signal ownership and clearing conditions aren't clearly documented. The safety functions are independently engineered and separate from this job interface.

3 replies

SA
SaraArcher0374
Replying to IsabelBaker0474

Does your trace show when the PLC request is raised and cleared relative to application polls, including which side performs the clearing?

7points
IS
IsabelBaker0474
Replying to SaraArcher0374

@SaraArcher0374 Our trace shows it rising and falling between two polls. The PLC clears it without an observed acknowledgement. No wonder the application misses it.

5points
SA
SaraArcher0374
Replying to IsabelBaker0474

Take an ownership table and a retained-request proposal to the interface owner. A request held until matching acknowledgement should settle the handshake in an offline review.

4points