FR10 handover pictures show a main routine and hide everything it calls

TobyBarnes0579 · 24 Aug 2026, 23:14 UTC

Reply to discussion
TO
TobyBarnes0579
Reference-plate inspection handover is mostly screenshots. No revisions, called routines, fixture assumptions or ordinary PLC expectations. Integrator still available. What do I ask for first?

5 replies

AA
AaronArcher0349
Replying to TobyBarnes0579

Request the identifiable running program package with its called routines, then have the integrator map the screenshots to it or mark their revision unknown. Use that package to build the dependency list.

14 points
TO
TobyBarnes0579
Replying to AaronArcher0349

Package received. One screenshot names a routine absent from the export. Asked whether export or picture is wrong.

13 points
AA
AaronArcher0349
Replying to TobyBarnes0579

Also check whether the main routine actually calls it in the supplied version. A picture may show an obsolete name, or the export may genuinely omit a dependency.

8 points
TO
TobyBarnes0579
Replying to AaronArcher0349

Integrator confirmed renamed routine. Call matches export; old screenshot identified. Fixture and PLC assumptions still missing.

7 points
AA
AaronArcher0349
Replying to TobyBarnes0579

Have the integrator walk one reference-plate cycle through that version with the responsible fixture and controls people. Record what each call expects and how an unmet ordinary condition appears to the operator.

2 points