Cannot tell support whether our spacer stop started at the tray

CalebBennett0754 · 1 Jan 2026, 05:44 UTC

Closed
CA
CalebBennett0754
Our UR5e pauses after lifting an aluminum spacer. Video starts after the pause. I can't tell support which signal changed first.

11 replies

LU
LucyCarter1002
Replying to CalebBennett0754

Does the controller history cover that occurrence? Start with what's already retained, including the application message. Another video of the stationary arm won't answer which signal changed first.

15 points
CA
CalebBennett0754
Replying to LucyCarter1002

History retained. Application says waiting for destination. My video only shows the spacer and arm.

21 points
CH
ChenBennett0703
Replying to CalebBennett0754

Who owns the destination tray signal? If the robot seller only supplied the arm package, this could sit in its queue while the person who wrote the tray logic never sees it.

6 points
CA
CalebBennett0754
Replying to ChenBennett0703

Our integrator wrote that bit. I've added them to the ticket with the same occurrence attached.

22 points
AL
AlexArcher0385
Replying to CalebBennett0754

Include what the operator saw at the tray, even if the answer is nobody looked. I've wasted time trying to align a phone clip with a log before discovering the clip was taken after someone had already moved the tray. It wasn't dishonest, just missing context. Mark any later reconstruction as later; don't let it quietly become the event everyone diagnoses.

11 points
LU
LucyCarter1002
Replying to AlexArcher0385

Alex, agreed about the clip. Caleb, did anyone move the destination tray before filming?

20 points
CA
CalebBennett0754
Replying to LucyCarter1002

Yes. Operator pulled it back to see the label. I'll add that; I hadn't asked him.

20 points
CH
ChenBennett0703
Replying to CalebBennett0754

Then leave its original position unknown. Who will show the next shift what to preserve if this happens again? The ticket needs someone on your side too.

5 points
JA
JaneChan1119
Replying to CalebBennett0754

Caleb, ask the integrator to explain the destination condition in terms your operators can recognise. A signal name alone can leave you collecting another technically correct but unhelpful report.

12 points
CA
CalebBennett0754
Replying to JaneChan1119

Integrator found a mismatch between the tray label and the insert fitted beneath it. Wrong insert wasn't reaching the intended sensing position. Correct insert fitted and their repeat check completed without that wait. I'm updating the changeover demonstration. The old clip still can't establish the tray's original position.

11 points
JA
JaneChan1119
Replying to CalebBennett0754

Was the wrong insert something the operator could distinguish during changeover, or is the labelling part of the fix as well?

19 points