Our FR10 bracket request has no agreed clearing owner

ChloeAllen0309 · 10 Apr 2026, 16:09 UTC

Closed
CH
ChloeAllen0309
We can miss the ordinary bracket inspection request between scans in our FR10 setup, and the proposed replacement still has both the PLC and application clearing it, so I need an agreed handover before changing the signal design.

1 reply

TH
ThomasBrooks0799
Replying to ChloeAllen0309

Have the two authors draw request, receipt and their clearing transitions on one sequence, including a delayed response. The monitoring view should observe those states without consuming them. Keep that ordinary job exchange distinct from the cell's safety functions

15points