Do I reteach this pickup or send it to maintenance?

LuisBaker0521 · 31 Dec 2024, 15:16 UTC

Closed
LU
LuisBaker0521
Our FR10 unloads plastic sleeves from trays. Pickup has been moved twice this month. Now one finger touches first even on an empty test position. I can change the point again but I don't think that's my job to guess.

5 replies

EL
ElenaAllen0340
Replying to LuisBaker0521

Have maintenance inspect the tool and tray location before another edit. Save the current teaching data and describe the one-finger contact. That gives them an observation to investigate instead of a third set of compensating points.

4 points
LU
LuisBaker0521
Replying to ElenaAllen0340

Saved it. With the cell isolated they found a packing strip under one tray stop. Fingers still looked wrong afterwards.

16 points
EL
ElenaAllen0340
Replying to LuisBaker0521

The strip may explain part of it. Ask them to check the finger mounting and wear as well, following the equipment procedure. Two faults can coexist; removing one doesn't prove the rest is sound.

11 points
LU
LuisBaker0521
Replying to ElenaAllen0340

Maintenance found a bent replacement finger. Wrong spare from our drawer. Correct pair fitted and they checked the setup before returning it. Picks are square again without my next masterpiece of teaching.

17 points
EL
ElenaAllen0340
Replying to LuisBaker0521

Label that drawer clearly and include the finger identification in the handover. The useful lesson for the next operator is that a new spare can still be the wrong spare.

3 points

Discussion closed