one acknowledgement, two possible inspection attempts

ClaraBrown0872 · 4 Sept 2026, 19:57 UTC

Reply to discussion
CL
ClaraBrown0872
I'm reading the logs from our UR5e fixture inspection after an application restart. Both attempts used the same job label. The acknowledgement could belong to either one, and the PLC clock is behind the laptop. Is there a way to reconstruct this without simply picking the nearest timestamp?

5 replies

EM
EmmaChan1072
Replying to ClaraBrown0872

Look for a sequence number or connection session first, because clock proximity can't distinguish two attempts sharing a label. Do any records carry one?

20 points
CL
ClaraBrown0872
Replying to EmmaChan1072

The laptop log has a session start line. The acknowledgement contains only the reused job label and result. PLC records show that label twice, with no attempt number.

18 points
EM
EmmaChan1072
Replying to ClaraBrown0872

Then record both possible associations unless another event rules one out. A tidy timeline would look reassuring, but it could still be the wrong story.

8 points
SA
SaraChen1157
Replying to ClaraBrown0872

We once found useful ordering in a connection-close record. Not a clock correction, just evidence that one response preceded a restart. Worth checking whether yours records that boundary.

15 points
EM
EmmaChan1072
Replying to ClaraBrown0872

For future attempts, ask the programmer for an identifier that survives restart and distinguishes retries; it won't recover the missing identity in this old acknowledgement.

18 points