fr5 inspection handover is mostly screenshots

PavelArcher0353 · 24 Oct 2025, 22:40 UTC

Closed
PA
PavelArcher0353
I need the installed revision and called routines for our bracket inspection. Screenshots cover neither. Integrator still available.

13 replies

CA
CarlaAbbott0053
Replying to PavelArcher0353

On an inherited fixture we found the screenshots described a different nest. Ask for the complete installed program export with its revision and the fixture assumptions, not simply more pictures of the main routine.

13 points
ME
MeiAdams0168
Replying to PavelArcher0353

And the ordinary PLC exchange needs its own description. We have just withheld a lesson until both sides demonstrated the agreed normal and interrupted behaviour. Buttons and screenshots were not enough.

21 points
PA
PavelArcher0353
Replying to CarlaAbbott0053

Requested both. The main routine calls inspect_bracket, which is absent from the supplied folder.

4 points
HA
HarishCarter1011
Replying to PavelArcher0353

Name that missing dependency in the request, so the integrator knows another copy of the main routine will not close it.

7 points
EL
EllaAllen0294
Replying to PavelArcher0353

Does the fixture shown in the screenshots match what is fitted? It may help to photograph the installed identifier now, while the integrator can explain any difference.

11 points
PA
PavelArcher0353
Replying to EllaAllen0294

Fixture label matches drawing D. Screenshots have no readable identifier, so I can't assign them confidently.

17 points
CA
CarlaAbbott0053
Replying to PavelArcher0353

Keep them as unverified illustrations until the integrator matches them. The current label and drawing give you a starting point, but the handover should describe the actual installed arrangement and its required checks.

4 points
ME
MeiAdams0168
Replying to PavelArcher0353

Can the maintainer open the eventual export with their normal account? We had a wonderfully complete folder that only the visiting person's setup could use.

18 points
HA
HarishCarter1011
Replying to MeiAdams0168

Mei, that check belongs in the handover session too, not just in an email saying the backup was delivered.

13 points
PA
PavelArcher0353
Replying to PavelArcher0353

Called routine arrived. Integrator matched revision 4 to the installed job. Maintainer-account check still pending. Ordinary signal table incomplete.

8 points
EL
EllaAllen0294
Replying to PavelArcher0353

Which part of the signal table is missing, Pavel? That may help you get a targeted answer before the integrator finishes their involvement.

16 points
PA
PavelArcher0353
Replying to EllaAllen0294

Who clears the inspection request and what acceptance means. Asked both program owners to agree those entries.

12 points
ME
MeiAdams0168
Replying to PavelArcher0353

Keep those meanings distinct from completion, and have the handover demonstrate an interruption as well as the neat exchange. We removed keep-pressing advice from our own lesson for a reason.

0 points

Discussion closed

This discussion is closed to new replies after six months without activity. Last activity: .